8:13, EEST
July 23, 2018
I have a controller from Sabo PLM and has OPC UA server integrated in it.I am able to connect my PLC with Prosys Client in my PC but when i try to connect with the Prosys android in my mobile it doesnt connect, what could be the possible reason.What technology is involved to connect my PLC with mobile if my server is itself my PLC .
10:36, EEST
Moderators
April 17, 2013
Hello,
The connection mechanism is completely same with PC based or Android based Prosys OPC UA Client.
First thing to check is that the network allows connection from the Android phone to the PLC. Meaning that there’s no firewalls or similar blocking the connection. As an example, try pinging the ip-address of the PLC from the Android phone.
Second thing to note is that you should start by testing the connection with security mode none and enable the security settings once the connection happens succesfully.
Most Users Ever Online: 518
Currently Online:
14 Guest(s)
Currently Browsing this Page:
1 Guest(s)
Top Posters:
hbrackel: 135
pramanj: 86
Francesco Zambon: 81
rocket science: 77
Ibrahim: 76
Sabari: 62
kapsl: 57
gjevremovic: 49
Xavier: 43
fred: 41
Member Stats:
Guest Posters: 0
Members: 681
Moderators: 16
Admins: 1
Forum Stats:
Groups: 3
Forums: 15
Topics: 1467
Posts: 6261
Newest Members:
graciela2073, sagarchau, elviralangwell4, Donnavek, Eddiefauth, DonaldPooma, fidelduke938316, Jan-Pfizer, DavidROunc, fen.pang@woodside.comModerators: Jouni Aro: 1010, Otso Palonen: 32, Tuomas Hiltunen: 5, Pyry: 1, Petri: 0, Bjarne Boström: 983, Heikki Tahvanainen: 402, Jukka Asikainen: 1, moldzh08: 0, Jimmy Ni: 26, Teppo Uimonen: 21, Markus Johansson: 42, Niklas Nurminen: 0, Matti Siponen: 321, Lusetti: 0, Ari-Pekka Soikkeli: 5
Administrators: admin: 1