Hi,
Are you sure you have the correct address?
I am only asking because I know that the Modbus addressing can be quite confusing. We don’t use entity numbers in addresses. Which means that address 18476 could mean digital input (entity number 1) address 8476. But if you mean input register address 18476 (a.k.a 318476) then that is fine too.
Have you tried other addresses?
If the other addresses are working but this particular one isn’t, then that means that the connection is OK, but the device does not support the address.
14:17, EET

January 30, 2020

Here is a link to Diris modbus registers
https://www.socomec.com/files/…..munication
From there i want to know total active power which is in my believe 18476 register.
I can also try with easier registers, if you have any recommendation.