Communication Error: https endpoints, OPC UA Sample Client and other simulation server
March 22, 2018
7:13, EET
Avatar
kate.rahul@gmail.com
New Member
Members
Forum Posts: 2
Member Since:
March 22, 2018
sp_UserOfflineSmall Offline

Hi,

We have downloaded latest OPC UA Source code on 21st March 2018, after compiling and executing OPC UA Sample Client and tries to communicate with OPC UA Sample Simulation Server (distributed by ProSys). We found below error while opening session,

Error: “Endpoint does not supported the user identity provided”.

We are using OPC UA Server (distributed by ProSys),
https://www.prosysopc.com/products/opc-ua-simulation-server/

However, we created one user in ProSys OPC UA Simulation Server, and we are using the same user authentication for communication with OPC UA Client over https endpoints.

Do we need to configure ProSys UA Server more to execute with OPC UA Sample Client over https endpoints?
How to test ProSys OPC UA Simulation Server for other OPC UA Clients?

If you need further information, please reply back.

Regards,
Rahul

March 22, 2018
14:48, EET
Avatar
Heikki Tahvanainen
Member
Members
Forum Posts: 402
Member Since:
April 17, 2013
sp_UserOfflineSmall Offline

Hi,

It sounds like the server is not accepting user identity tokens. So, check that the “Username&Password” checkbox is checked in User Authentication Methods. And also make sure that the setting is taken into use by restarting the Prosys OPC UA Simulation Server.

Other than that, please paste the actual stack trace of the error and we’ll be happy to provide more advice.

March 23, 2018
14:19, EET
Avatar
kate.rahul@gmail.com
New Member
Members
Forum Posts: 2
Member Since:
March 22, 2018
sp_UserOfflineSmall Offline

1. Checked the “Username&Password” checkbox is checked in User Authentication Methods, and restarted Prosys OPC UA Simulation Server.
–> Still its giving same error

2. Regarding stack trace, I can not paste images here, I have added the same issue on Git support for OPC UA Foundation as,
https://github.com/OPCFoundation/UA-.NETStandard/issues/411

On this link you may find exact stack trace by clicking on image

March 23, 2018
15:18, EET
Avatar
Heikki Tahvanainen
Member
Members
Forum Posts: 402
Member Since:
April 17, 2013
sp_UserOfflineSmall Offline

Hi,

Thanks for the information. According to my understanding, the issue is probably caused by the client application. So, it’s good that you have reported the issue to the Github repository.

If I understood correctly, you have already validated that the connection works with our Prosys OPC UA Client. If not, please fill the download form at our website (https://prosysopc.com/products/opc-ua-client/evaluate/) and validate that the connection works with this client application.

All this being said, I’d also like to mention that https communication is not widely used in OPC UA applications. The opc.tcp communication is much more widely used.

March 23, 2018
15:24, EET
Avatar
Heikki Tahvanainen
Member
Members
Forum Posts: 402
Member Since:
April 17, 2013
sp_UserOfflineSmall Offline

Actually, please ignore my last message.

Looking more closely to the picture that you have posted to Github, the client application tries to connect to

This is the opc.tcp endpoint. This endpoint will not accept https connections.

Instead, you need to connect to the https endpoint in port number 51443.

November 4, 2019
13:07, EET
Avatar
Viral
Member
Members
Forum Posts: 11
Member Since:
September 24, 2019
sp_UserOfflineSmall Offline

Hi,
I am trying to connect the prosys OPC UA server to prosys OPC UA client on the same machine.
When I try to connect both via UA TCP address client is getting connected, but when I try the same using UA HTTPS is “Cannot discover server application from…”.
Can you please help me with the problem?

November 4, 2019
14:15, EET
Avatar
Bjarne Boström
Moderator
Moderators
Forum Posts: 1032
Member Since:
April 3, 2012
sp_UserOfflineSmall Offline
Forum Timezone: Europe/Helsinki

Most Users Ever Online: 1919

Currently Online:
24 Guest(s)

Currently Browsing this Page:
1 Guest(s)

Top Posters:

Heikki Tahvanainen: 402

hbrackel: 144

rocket science: 88

pramanj: 86

Francesco Zambon: 83

Ibrahim: 78

Sabari: 62

kapsl: 57

gjevremovic: 49

Xavier: 43

Member Stats:

Guest Posters: 0

Members: 726

Moderators: 7

Admins: 1

Forum Stats:

Groups: 3

Forums: 15

Topics: 1529

Posts: 6471

Newest Members:

gabriellabachus, Deakin, KTP25Zof, Wojciech Kubala, efrennowell431, wilfredostuart, caitlynfajardo, jeromechubb7, franciscagrimwad, adult_gallery

Moderators: Jouni Aro: 1026, Pyry: 1, Petri: 0, Bjarne Boström: 1032, Jimmy Ni: 26, Matti Siponen: 349, Lusetti: 0

Administrators: admin: 1