Problem to connect with Backhoff OPC UA server
July 20, 2023
15:22, EEST
15:22, EEST

Bjarne Boström
Moderator
Moderators
Forum Posts: 1067
Member Since:
April 3, 2012
April 3, 2012

Hi,
Most likely it means it is in the https://reference.opcfoundatio…../docs/12.6 NO_CONFIGURATION state. In order for our SDK (that has been used to make the apps) work currently it needs to be in the RUNNING state.
Basically almost every server OPC UA just use the RUNNING state and maybe SHUTDOWN if they are shutting down.I think Bechoff was one of the few that use this no configuration state initially until configured.
Thus, basically you would need to make something on the server to make the state as RUNNING for it to work.