Hello
i have manage to connect your system to my 1x TRIO MC664X (FLOAT) and 1x EPACK (INT)
It’s working.
Now like i have mentioned in an another post, i would like to put in your server all my datas table i need (around 500 variables)
I have found the XML file like in the user manual pdf
I have open it with excel.
Now i would like to have
1) 1 exemple to fill your fil like my images send
2) how to use it ?????
Thanks
20:47, EEST
May 15, 2017
sorry
there is a problem with my files send and i don’t manage to erase them:
TRIO :
IP SETUP : http://hpics.li/a4950ea
DATAS : http://hpics.li/d9170b6
EPACK:
IP SETUP : http://hpics.li/9d13746
DATAS : http://hpics.li/10136bf
17:39, EEST
April 17, 2013
Hello,
You are correct that editing 500 variables by hand is not possible or convenient. For this reason, you can configure the Prosys OPC UA Modbus Server by editing the devicesConfig.xml file directly.
Actually the XML format has been designed to be very straightforward so that it would be easy to edit. Based on your description, it sounds like you have already found the devicesConfig.xml file in the correct folder (chapter 5 in user manual states the file locations).
Do you have some specific problem when editing the file?
12:48, EEST
May 15, 2017
Hello
yes i have found it.
To progress and to test all the communication of the the machine .
I woud like, if it possible for you, a filling exemple of this file according to my description mentionned.
– 2 Modbus master : TRIO + EPACK
– 2 type of différents variables (INT and Floatting with word swap)
Can you do it ?
Another question : When i make modification in the configuration. I dont see différences in this file.
How to upload devicesConfig.xml it in the server ??
Thanks
10:54, EEST
April 17, 2013
Hi,
I’m happy to send you an example of the configuration file by email. However, I think the actual problem is the description “When i make modification in the configuration. I dont see differences in this file.”
The functionality should be as follows: when you make changes in the user interface of Prosys OPC UA Modbus Server, the changes are immediately saved to the devicesConfig.xml. The changes are not taken into use before you restart the application. After restart, any changes that you made are taken into use. If you edit the devicesConfig.xml directly, the recommendation is to shutdown the application before making configuration changes. Otherwise it doesn’t matter whether the changes were done from the user interface or if you edited the devicesConfig.xml directly.
So to answer the question “How to upload devicesConfig.xml it in the server”: you need to restart the Prosys OPC UA Modbus Server in order to ‘upload’ the changes.
Please let me know if you experience any other behaviour than the description above.
16:10, EEST
May 15, 2017
Hello it’s perfect !
It’s Working well now.!
i have put this type of line :
VITESSE_PRODUCTION
LP1
I always compare your production to KEP OPC UA SERVER
and they use the possibiliy to comment each variables
It’s very usefull. Like you can see i have use it to have help.
– Can you put this fonction in the next version ?
– You mentionned you will change the polling time in the futur, have you got a date for this fonction ?
Most Users Ever Online: 1919
Currently Online:
18 Guest(s)
Currently Browsing this Page:
1 Guest(s)
Top Posters:
Heikki Tahvanainen: 402
hbrackel: 144
rocket science: 88
pramanj: 86
Francesco Zambon: 83
Ibrahim: 78
Sabari: 62
kapsl: 57
gjevremovic: 49
Xavier: 43
Member Stats:
Guest Posters: 0
Members: 734
Moderators: 7
Admins: 1
Forum Stats:
Groups: 3
Forums: 15
Topics: 1523
Posts: 6449
Newest Members:
christamcdowall, redaahern07571, nigelbdhmp, travistimmons, AnnelCib, dalenegettinger, howardkennerley, Thomassnism, biancacraft16, edgardo3518Moderators: Jouni Aro: 1026, Pyry: 1, Petri: 0, Bjarne Boström: 1026, Jimmy Ni: 26, Matti Siponen: 346, Lusetti: 0
Administrators: admin: 1